Would anyone know if this can be done. I don't want the batteries to be in my house in case I have issues with the batteries. Thinking of going with 6000XP and 4 51.2 server batteries. Either option A or B below. If I have it all in the house what precautions should I take?
 
Option A. Can you run 220 volt from the house panel to the 6000XP (6000XP stays in garage with batteries) and back to the house 35' away?
Option B keep the 6000XP in house and leave batteries in the garage? (would it be too much line loss)
Thanks Gregg
 
 

 
Posted : May 1, 2025 2:39 pm
Topic Tags
Ron
 Ron
(@ron)
Posts: 82
Estimable Member
 

You can do either option, but have to size the wire correctly. I would keep the batteries close to the inverter. https://www.southwire.com/calculator-vdrop

 