Question 12000XP Low Charge Rate Using Grid

2 Posts
1 Users
0 Reactions
9 Views
Posts: 2
Topic starter
(@usmcrtr)
New Member
Joined: 15 hours ago

I have a 12000XP with two indoor batteries and no solar.  AC Charge Battery Current(A) is set to 40A.  The system is used as a battery backup with grid pass through normally powering the load.  I would expect a much high charge rate.

SOC 66%
From grid: 2744w
To batteries: 2118w
Load: 454w

1 Reply
Posts: 2
Topic starter
(@usmcrtr)
New Member
Joined: 15 hours ago

I think I just found my answer but would like confirmation.  AC Charge Battery Current(A) set to 40A is 40A @ battery voltage and not 240v.