Silly question but I have to ask. On the right side of the invert there is a big red rocker switch. What position is that in. Could you post a pic?
@joel-brodeur I just trying to get the solar to do anything. I have no grid connection so there is the generator for ac charge mode, and the pv solar...
How many amps are you trying to draw. Everything looks set up correctly as far as I can tell from the pics. When you say AC charging do yo...
Thank you both for your comments. Joel is correct that what I wrote earlier means there is no NG bond at the generator - it was checked with a meter. ...
That makes sense. Thank you. To further the question, for touch potential, wouldn't you want the gen and chargverter to be at the same potential as...
I'm not sure what you mean by loads. The terminology to me means something else. I'm trying to learn as much as I can so I appreciate the explanatio...
@joel-brodeur here is the pictures.
@tristan I try to have all release notes added to this section of the forum: Firmware Updates – EG4 Community ForumHowever, I will see if I can find c...
Joel, Bonding means neutral connected to ground. In a ground fault situation you want the current to follow through the ground wire until it finds the...
Would you be able to provide a bit more information? What is/are you loads? What batteries do you have and how many? What solar panels do you ha...
On the monitoring sight go to maintenance, remote update and click on the "?" new window opens, click on "Check More" new page opens --> pi...
@jared Are there release notes for this firmware someplace? It would be nice to see what issues are being addressed before doing the update.
In general, it appears so. Would you have the spec sheets or a pic of the name plate? JB