Well, it did it again today; I have lost all remote communication with my 18Kpv as of about 3:05pm PDT. I was showing my wife some data on my phone ...
@wfbiggin I would not think that the RV has an NG bond but just for testing's sake, could you unplug the RV, make sure there is no power on in the RV ...
@joel-brodeur No worries. I'd be overjoyed if it was just that I overlooked something simple like that.
@wfbiggin Me being confused. for some stoopid reason I was thinking the 6000xp. Don't think (don't know) id 18K has one or not. Assuming not though...
@joel-brodeur I saw no settings in the 18kpv about NG bond - do you know where that setting is by chance and I'll check on that.
Hi, thanks for your reply. I believe this is what they are set at.. As for the invertor it's set to Battery Type 2: Lithium Lithium Typ 0: E...
@ron From my understand is that most do but then use a rectifier immediately at the source to provide DC. There are some that use DC generators. Th...
@wfbiggin When you added the physical NG bond, did you remember to disable the NG bond in the inverter? JB
I thought most wind turbines produce AC
Someone (@jared) posted that we should check out the EG4 tools site, specifically the "sizer" tool. I put in the specifics of my panels to see how...
The inverter firmware is fAAB-1E1E. Not sure which number is the battery firmware but bms is z02t13 and lcd 1.1.0 if those are the right numbers. vBat...
What protocol is configured on the batteries, and which lithium brand is selected on the inverter? Based on the screenshot, these appear to be Indoor ...
Feel free to DM your serial number and I can verify that it is correctly configured. However, this sounds normal for on-grid use.
I recommend reviewing our white paper on closed-loop versus open-loop systems for a detailed explanation. Personally, I prefer the BMS communication p...
What firmware version is currently installed on both the battery and the inverter? Also, which lithium brand is selected on the inverter, and what pro...