RE: Battery SOC inconsistancy

My 2-battery drift that way as well on SOC but definitely not that dramatically. I have seen posts on other forums about "resetting" the BMS's throu...

1 year ago
Forum
Reply
1 year ago
Topic
Replies: 2
Views: 835
Reply
RE: Grid pass through only or grid pass through with battery charging

When connected to the grid, the loads will switch to grid power if PV power is unavailable, and the battery reaches the on-grid EOD. To enable AC char...

1 year ago
Topic
Forum
Replies: 10
Views: 3109
Reply
RE: 6000XP EPS Outputs Shut Down Randomly When Battery Type set to Lithium, Getting Frustrated

It looks like the master inverter has less PV available then the secondary inverter. I would recommend making the inverter with two arrays as the mast...

1 year ago
Reply
RE: 6000XP EPS Outputs Shut Down Randomly When Battery Type set to Lithium, Getting Frustrated

Hi Jared, Thanks. When this happens my EPS output load is usually only 300 - 400 Watts. Sometimes lower. There are no errors listed in the Event Histo...

1 year ago
Topic
Reply
RE: 3 inverters in parallel A1, A2 & A3

The first inverter powered on will take the role of "master" inverter. However, if these are paralleled on the monitoring system, I would verify the s...

1 year ago
Reply
RE: Discharge Current Limit(Adc) 2 wall mounts and 3 6000xp's

I would recommend setting the discharge current to 350A with the two Wallmounts paralleled to the three 6000XPs.

1 year ago
Reply
RE: 6000XP EPS Outputs Shut Down Randomly When Battery Type set to Lithium, Getting Frustrated

Are any errors or warnings being reported when this is happening? My immediate thought would be EPS overload as the one Indoor Wallmount would not mee...

1 year ago