@brdfrd You're correct that due to the flat discharge curve of LFP using voltage is not an accurate way to determine SOC, mostly between the range ...
@brdfrd FYI, I have a battery bank of LL-S which is currently showing 98% (five batteries at 100%, and one at 90%). In reality, based on voltages, ...
@brdfrd Based on your last screenshot batt data, I think you are seeing the same problem as me. In reality, the batteries are remaining in sync and...
Question #9 has been moved to another thread under battery support.
@look4terry It sounds like you have a vendor that is trying to charge you for more stuff you don't need. Each of the batteries have a circuit brea...
Question #9 What is the discharge current measurement threshold for the LL-S BMS? I have encountered other LiFePO4 battery brands that have a relati...
I looked closer at your screenshot of the battery status. i just wanted to add here that like yours, my system while the SOC numbers are way out of ba...
@brdfrd The 112A figure above needs to be adjusted downwards to account for the charging efficiency of the 6000xp (93%) in order to prevent pulling...
@joel-brodeur I'm not using a 6000xp, I have an 18Kpv. And I'm using a very small 120VAC generator through a Chargeverter to recharge batteries in ...
@brdfrd That's 30amps of AC current, not DC. And since the sustained rate on the gen is 6,300, you should limit to 26 amps AC. But the setting th...
Following. I see similar issues using an 18Kpv and six LL-S batteries in an EG4 rack.
@mustangzrule sent it to you in a DM.
@mustangzrule That was it. I see it again now.