@jared Also, you didn’t answer the question about whether I should change charging control from “SOC” to “volt”. I’m inclined to change it to “volt...
@jared Thank you for your responses. Is there a way to see what charging voltage the BMS is calling for? The monitor displays the BMS charge curr...
Thank You @Jared for your responses here and in my other thread. So this is beginning to make sense to me. The EPS idle current of 1.37A DC, distrib...
@brdfrd Keep an eye on your cell voltages so you don't accidentally run one or two of the batteries into the ground. With the reported SOC numbers ...
@brdfrd You're correct that due to the flat discharge curve of LFP using voltage is not an accurate way to determine SOC, mostly between the range ...
@brdfrd FYI, I have a battery bank of LL-S which is currently showing 98% (five batteries at 100%, and one at 90%). In reality, based on voltages, ...
@brdfrd Based on your last screenshot batt data, I think you are seeing the same problem as me. In reality, the batteries are remaining in sync and...
Question #9 has been moved to another thread under battery support.
@look4terry It sounds like you have a vendor that is trying to charge you for more stuff you don't need. Each of the batteries have a circuit brea...
Question #9 What is the discharge current measurement threshold for the LL-S BMS? I have encountered other LiFePO4 battery brands that have a relati...
I looked closer at your screenshot of the battery status. i just wanted to add here that like yours, my system while the SOC numbers are way out of ba...
@brdfrd The 112A figure above needs to be adjusted downwards to account for the charging efficiency of the 6000xp (93%) in order to prevent pulling...
@joel-brodeur I'm not using a 6000xp, I have an 18Kpv. And I'm using a very small 120VAC generator through a Chargeverter to recharge batteries in ...