@joel-brodeur here is the pictures.
@tristan I try to have all release notes added to this section of the forum: Firmware Updates – EG4 Community ForumHowever, I will see if I can find c...
Joel, Bonding means neutral connected to ground. In a ground fault situation you want the current to follow through the ground wire until it finds the...
Would you be able to provide a bit more information? What is/are you loads? What batteries do you have and how many? What solar panels do you ha...
On the monitoring sight go to maintenance, remote update and click on the "?" new window opens, click on "Check More" new page opens --> pi...
@jared Are there release notes for this firmware someplace? It would be nice to see what issues are being addressed before doing the update.
In general, it appears so. Would you have the spec sheets or a pic of the name plate? JB
I am not a grounding expert so take all of as more of a question: I have noticed a mixed bag in NG bonding with generators. I always double check -...
@jared Forgot, in what scenarios the charging current in the inverter is not 100Amps? perhaps if using solar only ? thanks
@jared Just the answer i was looking for EXCELLENT, THANKS!!!!!!!
The equation for calculating charging time is ideally expressed as: Charging Time (hours)= Battery Capacity (Ah)/Charging Current (A)×Efficiency Fa...
The seven day one is kinda nice: it does break out each day into a separate sheet though, so you have to fiddle a bit to get it graph well. I ...
Even though your generator has a ground to earth terminal it may also be bonded from ground to neutral. Usually a wire inside the case.