RE: GFCI/AFCI breakers fail self-test when running from inverter only

I did some troubleshooting with an oscilloscope and have some interesting results. Here is a summarized test matrix and results: Run from wall (...

1 month ago
Reply
RE: GFCI/AFCI breakers fail self-test when running from inverter only

I think it is an AFI self-test feature as I have a 240 GCI only breaker that is stable and does not trip - leading me to the same hypothesis that you ...

1 month ago
Reply
RE: GFCI/AFCI breakers fail self-test when running from inverter only

Ok wait let's back it up for a second - at no point are these modes of operation occurring simultaneously - either the inverter LOAD breaker is OFF an...

1 month ago
Reply
RE: SOLVED Vbus Overrange Issue!

@CoolRunnings very neat find - I found this thread as I was wondering if anyone had added bus capacitance to the output of the 18K, but to solve a dif...