@daddydoug33 Could you post another pic of the screen showing the 8w?
I enabled setting 19 sorry. The pv off-grid
I would recommend checking if the PV input is cross polarized by measuring the voltage at the MPPT terminals. If the connections are cross polarized, ...
The default on that should have been 30 (I think). May I ask what you changed it to? JB
@daddydoug33 If you press the up or down button repeatedly you should be able to get the PV 2 to change to PV 1. Would you be able to do that and ...
I changed setting 6. Shows 8w from solar now.
Not that I am aware of. However, I will make sure to update the thread as soon as I have more information on this matter.
What are the VOC and ISC specs of the panel, and which inverter would they be connected to?
LCD V18 Changed the Gen overload on the alarm error page to AC overload. Changed the Meter type to Meter brand on advance interface. Modified th...
@herreraa, the charge current might be restricted through the settings, or the BMS could limit it based on the state of charge when communicating with...
@daddydoug33 can we please get a pic of your yellow and red PV switch on the right side? Oh, forgot to mention that you might want to check page...