So I installed the so-called correct version you linked above but now my 6kw panels are apparently outputting 45kW...a neat trick for a firmware updat...
Thanks Jared. But just to clarify: In example 1 where you wrote "AC coupling will not operate." I think you meant "AC charging will not operate". ...
for clarification:
If the wiring is the same as the 6000xp, then the manual is correct. The RSD button, requires a NO contactor. The text with the image is regardi...
The dry contacts for the external RSD are NO on the GND/RSD port.
I will verify this information and update it with the correct details for the RSD relay.
That looks like a mistake in the line diagram. I will be removing this from the post.
AC charge will be automatic once configured.
In that diagram, why is there a "PV System Disconnect" between the Main Breaker Panel and the LOAD terminal on the 12000XP?
Typically, a 4-6 AWG wire in conduit is used for the ground conductor. However, I strongly recommend confirming with a licensed electrician in your ar...
Currently, no specific diagrams are available. However, the 6000XP System Wiring Diagrams can be used as a reference, but you’ll need to size the brea...
Also, if frequency shifting is needed, I would recommend having the AC couple start SOC set in the range of 95-99% with the ending SOC set to 100%.
The System Charge SOC limit refers to the maximum allowable state of charge for the system. The Start and Stop AC Charge SOC settings define when the ...