Reply
RE: 12000xp and warning 28

Hello Set the system discharge rate to 100% last night. This morning ran another test. When the load went over 10220 watts the inverter gave the war...

1 month ago
Forum
Reply
RE: 12000xp and warning 28

That was my thinking as well. If I push the reset button the default setting is 10%. I’ve been increasing this setting by 10% after the inverter goes ...

1 month ago
Forum
Reply
RE: 12000xp and warning 28

Hello Eric First pic is the overview screen on the local monitor app Second is the local set screen under the discharge setting exspanded th...

1 month ago
Forum
Reply
RE: 12000xp and warning 28

Thanks Eric On the Local Monitor App Under the Discharge setting tab the “Discharge Current Limit(Adc)” is set to 250 Under the Discharge settin...

2 months ago
Forum
Reply
RE: Odd collection of EG4 Equipment…

Just curious, could you AC couple the 6000xps to the 18Kpv?

2 months ago
Reply
RE: 12000xp and warning 28

Further observations Had the load up to 7800 watts. The battery was running over 7K watts and no warning 28. So now I’m wondering if this “System D...

2 months ago
Forum
Reply
RE: 12000xp and warning 28

Hello 12000xp updated firmware 405 I believe. In the local monitor app there is a setting under “Discharge Setting” called “System Discharge Power...

2 months ago
Forum
Topic
Forum
Replies: 11
Views: 286