RE: 12000xp and warning 28

@eg4newbie just a quick note. Bypass limit is 100 amps ac, but the inverter can only produce 50 amps ac before overload is reached, even less if ba...

5 days ago
Forum
Reply
RE: 12000xp and warning 28

@eg4newbie One clue for me is that the bypass power from grid was 6329 watts. This would cause an overload warning if that load was on one line, and...

6 days ago
Forum
Reply
RE: 12000xp and warning 28

@eg4newbie Short answer, I don’t know. The PV has to be higher than the load by a certain margin, as there is an overhead cost, and I think this i...

7 days ago
Forum
Reply
RE: 12000xp and warning 28

@eg4newbie When the SOC reaches 100% the BMS turns off charging. I’ve noticed that sometimes the PV will take a few minutes to turn back on to full ...

1 week ago
Forum
Reply
RE: 12000xp and warning 28

@eg4newbie your 12000xp still isn’t changing the battery BMS from the 200 amp discharge setting is it? On battery only and balanced lines you can ...

2 weeks ago
Forum
Reply
RE: 12000xp and warning 28

Hello Eric, The inverter is setup for 250 discharge, but this is not changing the BMS on the battery to 250 amp discharge. These are MNPowerflo 5 ...

4 weeks ago
Forum
Reply
RE: 12000xp and warning 28

Hello, time for a little update. Now have 4 batteries hooked up in parallel and plugged into the inverter com port. the inverter shows 4 batteri...

4 weeks ago
Forum
Reply
RE: 12000xp and warning 28

Hello Set the system discharge rate to 100% last night. This morning ran another test. When the load went over 10220 watts the inverter gave the war...

3 months ago
Forum
Reply
RE: 12000xp and warning 28

That was my thinking as well. If I push the reset button the default setting is 10%. I’ve been increasing this setting by 10% after the inverter goes ...

3 months ago
Forum
Reply
RE: 12000xp and warning 28

Hello Eric First pic is the overview screen on the local monitor app Second is the local set screen under the discharge setting exspanded th...

3 months ago
Forum
Reply
RE: 12000xp and warning 28

Thanks Eric On the Local Monitor App Under the Discharge setting tab the “Discharge Current Limit(Adc)” is set to 250 Under the Discharge settin...

3 months ago
Forum
Reply
RE: Odd collection of EG4 Equipment…

Just curious, could you AC couple the 6000xps to the 18Kpv?

3 months ago
Reply
RE: 12000xp and warning 28

Further observations Had the load up to 7800 watts. The battery was running over 7K watts and no warning 28. So now I’m wondering if this “System D...

3 months ago
Forum
Reply
RE: 12000xp and warning 28

Hello 12000xp updated firmware 405 I believe. In the local monitor app there is a setting under “Discharge Setting” called “System Discharge Power...

3 months ago