Question 12000XP LOAD (EPS) Breaker Trip Rating / Setting

4 Posts
3 Users
0 Reactions
60 Views
(@john-p-carroll)
Active Member
Joined: 2 months ago
Posts: 3
Topic starter  

I have a new unopened 12000XP. Buying wire / cable. How many amps is the load breaker capable of / trip point in amps. if there is nomenclature near it indicating this, it is not visible on the datasheet, manual or website pics I've found. Would someone look at theirs & advise, please? THANKS!


   
Quote
(@john-p-carroll)
Active Member
Joined: 2 months ago
Posts: 3
Topic starter  

Since the 12000XP has a feature published as '100 Amp Pass-Through', does that mean that all of the 100 amps grid can be passed through (out) the load breaker and this would require sizing the load cables accordingly for 100 amp continuous, same as the grid?


   
ReplyQuote
Mikes Garage
(@mikes-garage)
Active Member
Joined: 3 weeks ago
Posts: 7
 

The 12000XP can output approximately 50 amps continuous and 75 amps peak.  I use an 80 amp breaker in my combiner box (for paralleling) but my shop is completely off-grid so there is no pass-through.  I have several video's wiring up a 12000xp including how to parallel them.  My Youtube is https://www.youtube.com/c/MikesGarageRoute66  

This post was modified 3 weeks ago by Mikes Garage

https://www.youtube.com/c/MikesGarageRoute66
https://www.windsolarforum.com


   
ReplyQuote
(@pgaffney)
Active Member
Joined: 1 day ago
Posts: 3
 

The "Load" disconnect breaker on the 12000xp is 100 Amp. AWG of the wire connecting to that breaker must be capable of carrying 100 Amps.  I believe that is a "code" requirement.   If you are back-feeding a sub panel - the breaker on the sub-panel side could be a lower amp value.


   
ReplyQuote