I have an 18K inverter. When using PV and battery to power loads (Standby) and back feeding the mail panel (House), the
power flow arrows only point to the house icon. Is there a way to show arrows to both the "Standby" (Loads) and mail panel (House) at the same time. The grid power is available at this time but not being used. On the Phone App there is an EPS area which has " EPS L1N:" and EPS L2N:" but show no values in watts.
Thanks,
Matt
From the Monitor website.
"It is for absolute zero-export, when there is an AC connection. When enabled, the battery discharges power to load first and the grid will not assist in powering loads and the batteries will not charge from AC unless 'AC charge' is enabled."
So when the batteries are depleted the loads will be powered off. There will be no back feeding to the grid panel.
I'll keep the system as configured and install a couple of separate CT coils and displays to monitor the load outputs.
Eric, Thanks for the verification.
Thanks,
Matt