Question 6000xp Not Recognizing New Battery

5 Posts
2 Users
0 Reactions
94 Views
(@texasoffgrid)
Active Member
Joined: 3 weeks ago
Posts: 3
Topic starter  

EG4 Family,

I have 9 batteries: 5 each 48V EG4 LIFEPOWER4 V1, 3 each V2 (with dip switches), and a replacement V2 (without dip switches).   

The new V2 (w/o dip) was a replacement for a V1 that failed. I placed the new V2 as #4 in my stack, so all the V2s come first, then the 5 V1s.

The new battery is charging and discharging, and passing through comm to the following batteries.  But here is the problem:

My two 6000XPs do not "see" the new V2 battery (w/o dip switches). The system reads 8 batteries and 800 amps, when it should read 9 batteries and 900 amps.  The battery/inverters show no alarms, and the battery is charging and discharging with all the other batteries. I tried turning everything off/on, but no change. Since there are no dip switches, I set all the other battery dip switches and skipped #4 assuming the battery would automatically take that number.  But the EG4 Monitor Center does not show a #4 battery. 

Does anyone have any idea on how to make the new V2 (no dip switches) battery visible to the system? 

Thanks for your help,

Scott   



   
Quote
EG4 Eric
(@eg4eric)
EG4 Online Support Admin
Joined: 1 year ago
Posts: 1057
 

Try putting the new V2 batteries without DIP switches as the master and the #2 battery. Then set the V2 with DIP switches and then the Lifepower4-V1. This is the order the batteries should be in. 



   
ReplyQuote
(@texasoffgrid)
Active Member
Joined: 3 weeks ago
Posts: 3
Topic starter  

@eg4eric 

Thanks, I'll give it a try and let you know if that clears it up.

Scott



   
ReplyQuote
(@texasoffgrid)
Active Member
Joined: 3 weeks ago
Posts: 3
Topic starter  

Hey, moving the V2(no dip switches) to the master battery position worked like a charm: 9 batteries/900 amps shown!

However, in an interesting twist, my 5 V1 batteries are now constantly showing 51% SOC in the Monitor Center.  I think I saw this particular issue mentioned in another thread, so I'll do some digging.

Thanks,

Scott



   
ReplyQuote
EG4 Eric
(@eg4eric)
EG4 Online Support Admin
Joined: 1 year ago
Posts: 1057
 

@texasoffgrid 
You will need to update the Lifepower4-V2 batteries. Make sure you choose the correct firmware to download. 

EG4 LifePower4 48V v2 - EG4 Electronics