EG4 18KPV parameter help?

2 Posts
2 Users
0 Reactions
79 Views
(@gregm)
Active Member
Joined: 1 month ago
Posts: 3
Topic starter  

The way I would like my EG4 18KPV to work is that the grid would not input any power until the battery charge falls to 20 or 25% (maybe in the middle of the night) and then it would turn on and charge the batteries.

What parameter(s) is it that would control this and what should I set it to?

The Ruixu pamphlet says "The Low Voltage cut-off" is 44.8v

This topic was modified 1 month ago by GregM

   
Quote
EG4 Eric
(@eg4eric)
Honorable Member
Joined: 9 months ago
Posts: 479
 

Ensure that Battery Backup Mode is disabled, verify that you have sufficient solar and battery capacity to support your loads, and set the On-Grid Cut-Off SOC (%) to 20% or 25%.


   