I hope just a simple question.
When the CT coils detect that the grid has lost power, can any power from battery or solar
feed back thru the back feed breaker. I would expect this to not be possible. Is there any
documentation to verify this ?
Thanks,
Matt
When the grid goes down, the inverter prevents power from feeding back into it. Here’s a link to a document that explains this in more detail.
Please let me know if you need anything else.
EG4-18kPV-12LV-Manufacturers-Anti-Islanding-Method-Secured.pdf
Thanks Eric,
That makes me feel more comfortable with the safety of
the lineman working to restore the grid at some point.
Matt
Absolutely! That’s a common question. You can find a lot of helpful documents available on the product page in case you have any other questions about the product.