new battery not being recognized on Device Monitor

2 Posts
2 Users
0 Reactions
46 Views
Posts: 2
Topic starter
(@bwpsg42)
New Member
Joined: 2 months ago

My system is a pair of 6000XPs in parallel, a LL battery#1 and 3 lifepower batteries#3,4,5.  All have been working properly and 400AH recognized as near as I can tell. Today I added a second LL battery as #2.  I see no change in what is shown on monitor  using the web access.  I restarted the master 6000 after adding the battery into the comm string. The fw is the same on both LL and the lifepower fw was updated to work thigh the LL when I added it. As I mentioned in a comment on another thread earlier today,  the battery info section has never displayed anything on my system.  What have I missed with this battery addition.  All 5 hit 100%SOC this afternoon.

Screenshot 2025 02 08 at 6.04.06 PM

 

1 Reply
Eric
Posts: 73
 Eric
(@eric)
Trusted Member
Joined: 4 months ago

If you have the protocol set to 0 on the inverter, you can try changing it to 1 and see if that helps. Just a warning that making this change will restart your system and you will lose power for about a moment. 

Reply