Question Time+SOC doesn't trigger AC Charge

3 Posts
2 Users
0 Reactions
66 Views
Posts: 23
Topic starter
(@powerup)
Eminent Member
Joined: 5 months ago

12kPv (fw: EAAB-2021) + two 14.3 KW wall mount (Closed Loop / Volt)

Application is TOU exclusively. For the time being I have "Batt Charge Control" set to "Volt"

      "AC Charge Based On" set to "Time"

Every morning the Inverter has started its charge on time @ 09:30

Last night I decided to set the "AC Charge Based On" to "Time+SOC/Volt"

       I was told by SS that this setting means it will be scheduled for Time OR SOC/Volt

The Inverter did NOT start at 9:30, I finally went in to settings, changed the "AC Charge Based On" back to "Time" only and then reset the start time to be 2 minutes beyond that moment.

       The inverter then started to charge (as expected)

Am I misinterpreting "Time+SOC/Volt"? This was the ONLY adjustment made.

Appreciate guidance, welcome to test options to help identify potential anomaly 

2 Replies
1 Reply
(@krzysiek_kta)
Joined: 7 months ago

Eminent Member
Posts: 20

Posted by: @powerup

12kPv (fw: EAAB-2021) + two 14.3 KW wall mount (Closed Loop / Volt)

 

In my experience when Wall Mount battery is set to lithium (closed loop) the battery voltage settings do not work - only SOC triggers charging: "Battery SOC and Time (according to)"

On the other hand when battery is set to Lead Acid (open loop) only Voltage settings work:

"Battery Voltage and Time (according to)", SoC doesn't do anything.

 

Hope that helps.

 

Brgds

 

K

 

Reply
Posts: 23
Topic starter
(@powerup)
Eminent Member
Joined: 5 months ago

Thank you, I was thinking it could be conflicting with another setting.

Reply