Posts: 29
Topic starter
(@scottmr808)
Eminent Member
Joined: 10 months ago

6000XP with the wallmount battery, newish install. Seemed fine when I was there on the install, but may not have stayed long enough to see the issue. Client called and said that every 10 ish minutes the inverter drops AC output for a few minutes. I went to the site and sure enough it happened while I was there. Inverter kicked off AC and then displays warning 27. Occasionally trips battery breaker according to client ....  any clues?   Otherwise charges up fine from PV.    station name: Puamanu

31 Replies
EG4 Eric
Posts: 553
(@eg4eric)
Honorable Member
Joined: 10 months ago

Warning 27 indicates either a low battery voltage or a communication issue between the battery and inverter, preventing the inverter from receiving the correct data.

  • Make sure you have the Lithium Type set to 1.
  • Make sure the battery is charged, and that the voltage is above 40V.

    Let me know if this helps or if you need further assistance!

Reply
3 Replies
(@scottmr808)
Joined: 10 months ago

Eminent Member
Posts: 29

@eric Is the battery type something you can remotely change? This inverter is very remote ...... I thought it was 0 for EG4 on the 6000xp and 1 for 12000xp but the last 12000xp I set up at latest firmware seemed to show 6 for EG4 .... so a bit confused here. The station name is listed in my prior post if you can find it, otherwise I will swing by Saturday and set it to 1.

Reply
EG4 Eric
(@eg4eric)
Joined: 10 months ago

Honorable Member
Posts: 553

@scottmr808 
For the WallMount batteries, the Lithium type will be 1 for all the inverters. 

I did see that you were able to change it. Has your client had anymore issues?

Reply
(@scottmr808)
Joined: 10 months ago

Eminent Member
Posts: 29

@Eric   Aloha Eric, I was able to go to site and change it. Waiting for results, crossing fingers!  Thank you

Reply
Posts: 29
Topic starter
(@scottmr808)
Eminent Member
Joined: 10 months ago

Unfortunately client reports it continues to drop out power ...  they said 2pm 5pm and 9pm it reset yesterday.  One thing comes to mind .... the 6000xp only has single battery lugs, so there is only a single 2/0 cable going to the powerwall. Do I need to make a busbar out of the two provided 2/0 cables and then run a 4/0 cable into the 6000xp lugs?  @eric is there a way to dial in and check out what is happening?

Reply
19 Replies
EG4 Eric
(@eg4eric)
Joined: 10 months ago

Honorable Member
Posts: 553

@scottmr808 
I did take a look at the system but did not find anything indicating that the system is losing power. I don't see any warning or fault codes. 

What is the protocol set to on the battery? This sound like it could be a communication problem between the battery and inverter. Are they turning anything on when this happens?

Reply
EG4 Eric
(@eg4eric)
Joined: 10 months ago

Honorable Member
Posts: 553

Can you post some pictures of the system and maybe how it's wired as well? I don't see anything indicating the power going out.

I recommend deep cycling the battery down to 20% at least once a week. You may need to switch the protocol to lead acid mode to help balance the battery cells, as 100% is currently showing at 53V when it should be around 56.2V. This will also help determine if the power loss is due to a communication issue.

Reply
(@scottmr808)
Joined: 10 months ago

Eminent Member
Posts: 29

@eric Hello Eric, I changed the system to lead acid battery type and customer reports it seems to have resolved the issue of it dropping out once or twice a day for 10-15 seconds. I did not get picks of the wiring as I did have the time pull the cover, but its a very basic install as there is no grid, no generator cord. I will go there this weekend and draw it down to 20%, and can pull the cover for pics for you. I will post a few pics then .... So if its a comm error, should I try to replace the comm cable after the SOC gets closer to the actual voltage and then swap it back to lithium iron ?

Reply
EG4 Eric
(@eg4eric)
Joined: 10 months ago

Honorable Member
Posts: 553

@scottmr808 
i recommend leaving it on lead acid for a few days and make sure that the battery is charging fully to 56.2V and discharging to about 48-49V. 

After this, you can switch it back to lithium and just make sure that the communication cable is connected correctly and that the protocol on the inverter is set to 1 and EG4/LUX (CAN) on the battery. 

Yes, please post some pictures, if possible, to make sure the cables at the correct ones and that everything is good to go.

Please keep me updated.

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

@eg4eric 

 

I am having very similar issue with my setup - contacted distributor and eventually got the RMA and received replacement 6000xp, yet the power loss events while off-grid still occurred with battery type set to lithium.

Note - the setup was working flawlessly mid-Jan'25 till mid May25' then the issues started.

I am currently on Lead Acid battery setting and cycling it 20-100-20% SoC. Will post results after switching back to Lithium type 1 afterwards

 

Thanks for advice.

 

 

Brgds

 

K

Reply
EG4 Eric
(@eg4eric)
Joined: 10 months ago

Honorable Member
Posts: 553

@krzysiek_kta 

Please let me know if it stops or if you continue to have issues!

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

@eg4eric 

 

Touch the wood - all works back as it supposed to.

Thanks Again for the tip of cycling the Wall mount battery in lead acid mode and switching back to Lithium type 1.

In my case it seems to solve the issue. Yesterday after completing cycling the battery  20-100-18% SoC in Lead Acid mode I switched Lithium type 1 in settings and..... will post if anything changes but all seems solid so far.  

After switching to lithium battery I had the 0x4000000 warning logged and I decided to restart the inverter. Eventually and after an hour or so it cleared and... all works so far - within last 24 hrs no traces of power losses nor charge interruptions nor correlated "vact" values drops as experienced before since the issue emerged last month.

Thanks again @EG4eric.

I think your advices should be included or at least referenced in online manual for EG4 6000xp with wall mount indoor battery.

Best regards

 😀 K

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

UPDATE 😕

After 24 hrs of smooth operation with lithium type 1 battery setting the inverter resumed periodic power losses when in off-grid mode 2-5 times a day.

Switched the battery type to Lead Acid - no single issue since then. Currently in process of deep cycling the battery 0%-100%-0%-100%. After that I will give it another try in Lithium type1 battery setting and see how it goes.

 

Brgds

K

 

Reply
EG4 Eric
(@eg4eric)
Joined: 10 months ago

Honorable Member
Posts: 553

@krzysiek_kta 
If the issue occurs again after switching back to Lithium 1, please send me your inverter's serial number so we can investigate further and determine the cause.

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

@eg4eric 

THX - will do. 

Currently I am still on Lead Acid battery type mode - no problems whatsoever (just lack of SoC on App/Web - yet the wall mount battery display shows somewhat close to reality SoC - at one point of deep cycling process it showed 0% at 48V battery and the system was still on until my cut-off setting of 47V kicked in).

After I decide to switch back to Lithium - type 1 will let you know if problems persist.

 

THX again

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

UPDATE 😓 

I have been running on Lead Acid for last week did two full cycles of deep discharging down to 0% and then charging to 100%.Today after last deep cycle switched back to Lithium type 1 and within six hours recorded three (3) instances when there was 2-3s loss of power while off-grid.

Deep cycling the wall battery did not help. I suspect the BMS is to blame.

Will re-open ticked wit vendor (Signature).

Life.

 

K

 

Reply
EG4 Eric
(@eg4eric)
Joined: 10 months ago

Honorable Member
Posts: 553

@krzysiek_kta 
If provide your inverter's serial number, I can also take a look at the data and try to identify what could be causing this issue.

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

@eg4eric 

 

PM sent

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

@scottmr808 

 

Have heard anything form EG4 regarding resolving the EG4 wall mount battery BMS comms issue - causing those irregular power losses?

 

Brgds

 

K

Reply
(@scottmr808)
Joined: 10 months ago

Eminent Member
Posts: 29

@krzysiek_kta They had me run Lead Acid for awhile, and indeed while it was Lead Acid no issues. However, recently swapped back to Lithium type 1 and now its happening again, sigh .... nothing on the app in the events section, going to drive down there and check the power wall logs.  Super frustrated ..... have installed dozens of these 6000xp inverters, but admittedly only a few that are using the power wall instead of the server rack batteries.

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

@scottmr808 

It seems to me that there is comms issue with EG4 Wall Battery BMS, and not related to the Inverter as I have replaced my 600xp and others with GridBOSS & FlexBOSS are reporting same problems and Lead Acid battery settings solve the power blip/blackouts.

@eg4eric

This issue is easily detectable only in off-grid mode as it causes blackouts, when the inverter is grid connected it will not be noticeable easily  - no blackouts, just charging interruptions if within charging period.\

I bet there is many, many more users affected, but  only the off-grid ones suffer (I had to install UPSs for critical loads and whole house surge protection to prevent of my electronics failing before I settled to Lead Acid mode battery type)

I think it is time to rise the ticket and let EG4 address this issue

 

Reply
(@scottmr808)
Joined: 10 months ago

Eminent Member
Posts: 29

@krzysiek_kta I totally agree. Be nice if the latest firmware had a fix for this, but last I checked there was nothing mentioned.

Reply
(@ronster)
Joined: 2 weeks ago

New Member
Posts: 4

Posted by: @scottmr808

@krzysiek_kta They had me run Lead Acid for awhile, and indeed while it was Lead Acid no issues. However, recently swapped back to Lithium type 1 and now its happening again, sigh .... nothing on the app in the events section, going to drive down there and check the power wall logs.  Super frustrated ..... have installed dozens of these 6000xp inverters, but admittedly only a few that are using the power wall instead of the server rack batteries.

@krzysiek_kta

@scottmr808

Is there any downside or damage to the 12000xp equipment by operating in the "Lead Acid" mode to bypass this glitch?

 

Reply
(@krzysiek_kta)
Joined: 9 months ago

Eminent Member
Posts: 32

@ronster 

I was told by SS tech that Lead Acid Battery mode is an open loop communication mode (manual mode) and aside some lost functionality (lack of SoC) it does not affect the battery performance nor affect its warranty.

 

Reply
Posts: 29
Topic starter
(@scottmr808)
Eminent Member
Joined: 10 months ago

@eric  it was setting the warning 27 when I was there but it cleared up very quickly and then restarted providing power. Not sure if its still setting a 27 when it is happening now. The protocol on battery was set to CAN EG4/LUX ..... I don't think there is any correlation with loads, when I was there was literally just LED lights on in house and no client activities. Maybe a refrigerator compressor could have kicked on or something but nothing obvious. They are used to living on battery backup and don't have any high draw appliances.  Is there a log on the battery itself that I can view somehow or displayable on the Inverter without having the station on my phone?

Reply
1 Reply
Joel Brodeur
(@joel-brodeur)
Joined: 11 months ago

Reputable Member
Posts: 352

@scottmr808 If you are able to check on the inverter - Setting 22 sub-settings AREC and EREC, you may find additional information (other faults or warning being thrown).  It will cycle through the date time and record.  Kind of a pain but it can be useful.  Also, you may try swapping out com cable(s).  Double check that the cables are run to the correct ports.  Make sure that there are no "tight" windings on the cable, no sharp bends etc.

When I have run into persistent comm issues, one thing I do is to remove the comm cable from all raceways - unplug it fish it back out of system and run from bat to inverter in open space to avoid any interference from other cables.

Just some ideas....

 

Reply
Joel Brodeur
Posts: 352
(@joel-brodeur)
Reputable Member
Joined: 11 months ago

Posted by: @scottmr808

Is there a log on the battery itself that I can view somehow or displayable on the Inverter without having the station on my phone?

There are logs on the battery, as far as I know they are only accessible through the touchscreen on the battery.

Reply
2 Replies
(@scottmr808)
Joined: 10 months ago

Eminent Member
Posts: 29

@joel-brodeur thank you, I checked last time did not see anything accessible but perhaps did not look close enough and will try again next visit

Reply
Joel Brodeur
(@joel-brodeur)
Joined: 11 months ago

Reputable Member
Posts: 352

@scottmr808 On my batteries the logs are under settings-logs.

But for some reason my batteries have a strange firmware installed.  Not certain why or what it means (still waiting on an answer for it).

I will double check here in a bit and let you know what I see on mine.

Reply