As the picture shows below, I have 3 18KPV's, 2 outdoor wall mount batteries and 4 indoor batteries. All will be connected to a FlexBoss. Does this battery wiring work?
As the picture shows below, I have 3 18KPV's, 2 outdoor wall mount batteries and 4 indoor batteries. All will be connected to a FlexBoss. Does this battery wiring work?
This would not be able to work due to the internal bus bars being limited to 600A. However, there are some alternatives. You can use external bus bars (Would have to be rated more than 700A) and connect all the batteries together and then distribute them to all 3 inverters, or you can connect 2 batteries to each inverter.