I have EG4 off grid system consisting of 1 Flexboss21, 2ea 280 AH wall packs, 2 chargeverters, solar and a 13 kw kubota generator. Both chargeverters and batteries are connected to a 400 amp busbar. 1st chargeverter is communicating through RS 485 with Master battery and charging according to SOC and starting generator at 20% SOC through NO consctacts. Second chargeverter will not communicate with slave battery. What the best way to set up the second chargeverter to coordinate charging. Any help would be greatly appreciated 

Jim


7 Replies
EG4 Eric
Posts: 1035
Admin
(@eg4eric)
EG4 Online Support
Joined: 1 year ago

Are you communicating both batteries with the inverter? 

Usually, the batteries can either communicate with the inverter or the chargeverter. you will need to either need to the chargeverter to charge by voltage or set the inverter to operate based on voltage. 


Reply
4 Replies
(@powelljn50)
Joined: 9 months ago

Active Member
Posts: 4

@eg4eric 

I have batteries paralleled and communicating. The RG485 is connected to the 1st chargeverter annd master battery. It is set to start generator through N/O contacts to charge at 15% SOC. The other chargeverter RS485 is connected to the second battery with charge on/off set to voltages. The CAN port is connected to the Master battery and Flex21  Both batteries and chargeverters are connected to a 600 amp buss. Is there any way to get the second chargeverter to charge by SOC to copy Master battery ? Should I connect the chargeverters in a different configuration? 
Thanks


Reply
EG4 Eric
Admin
(@eg4eric)
Joined: 1 year ago

EG4 Online Support
Posts: 1035

@powelljn50 

If the batteries are communicating with the inverter, you would need to set the Chargeverter to charge the batteries by voltage. Since the batteries cannot communicate with both inverter and Chargeverter at the same time. Having everything connected to bus bars is correct.


Reply
(@powelljn50)
Joined: 9 months ago

Active Member
Posts: 4

@eg4eric 

Thanks Eric,

    I have the master battery communicating with the chargeverter through the RG485 port and the Can port on master battery to the Flex21. The second battery and chargeverter are connected through the RG485 port, set to voltage and linked to the master battery through the battery com ports. What would be the correct voltages to set for start and end charge if looking to start at 15% SOC and end at 100% SOC? Thanks much


Reply
EG4 Eric
Admin
(@eg4eric)
Joined: 1 year ago

EG4 Online Support
Posts: 1035

@powelljn50 
Because your batteries are communicating with the inverter already, there is no need for the communication cable between batteries and chargeverter.

For 15% the battery voltage would need to be set around to around 49V-50V and 100% would be at 56.2V


Reply
Posts: 4
Topic starter
(@powelljn50)
Active Member
Joined: 9 months ago

For consideration: Flex-boss 21 would be better served if it had a way to start a generator or manage multiple chargeverters in an off grid scenario, without buying a GridBoss. 


Reply
1 Reply
EG4 Eric
Admin
(@eg4eric)
Joined: 1 year ago

EG4 Online Support
Posts: 1035

@powelljn50 

Thank you for the feedback. I’ll be sure to share this with our team. The FlexBoss is designed to be installed alongside the GridBoss, though it can operate as a standalone unit. When used on its own, you cannot connect the generator to the inverter. Other than that, it will work as an inverter like the rest of them.