How does the 6000xp decide to pass through grid to the loads or pass through grid to the loads and also charge the battery?

What are the settings needed?

I want to obviously use all of the power the solar panels create, but if I run out of battery a few hours before the panels start to produce power I don't want the grid fully charging the batteries. So many variables

3 Replies
Jared
Posts: 150
Moderator
(@jared)
Online Support
Joined: 2 months ago

When connected to the grid, the loads will switch to grid power if PV power is unavailable, and the battery reaches the on-grid EOD. To enable AC charging, you’ll need to activate it either through the LCD display or the monitoring system.

image

 

image
Reply
Ron
Posts: 33
 Ron
Topic starter
(@ron)
Trusted Member
Joined: 1 month ago

So grid charge is completely manual function?

Reply
Jared
Posts: 150
Moderator
(@jared)
Online Support
Joined: 2 months ago

AC charge will be automatic once configured.