Anyone else notice this or are you able to use electricity when using a generator to recharge your batteries?
@frugal-farmer What inverter are you using?
Sometimes the easiest solution is the best solution.
Sometimes not.
I saw another post of yours, looks like you are using the 3000EHV?
I am not familiar with them nut based on the manual I am guessing that maybe setting 16?
Sometimes the easiest solution is the best solution.
Sometimes not.
16 is at SNU. Thanks but checked that already. Guess I will call Signature Solar soon. If they can fix these with software I will report back here what their findings were.
Do you have setting #3 set to GNE?
Sometimes this does require a firmware update depending on what firmware the inverter is on.
Thanks, yes...3 is a GNE.
We have finally figured out what was stopping utility/generator charging when NOT in "standby mode"! A tech over at Signature Solar advised lowering setting 43 (point back to utility) from it's original setting of 50% batteries charged state to 25%. Apparently we had been testing with the batteries always above 50% charged. Setting it to 25% has even allowed charging past 50% if/when desired.