@in-offgrid-greenhouse On that graph, or someplace else in the app, can you identify a point in time (or a few) and let us know what your actual bat...
@in-offgrid-greenhouse OK, then I don't think you have a SOC drift problem - your baseline discharge current of ~6A is high enough to avoid it. F...
@jlankford Load varies between 300W to 500W for some low power heaters in a chicken coop. 1 heating unit stays on all the time, the other unit comes o...
@ray I used the battery cables provided in the box, which are 5awg. Some numbers: Max system current: 280 A DC Max current per battery: 47 A DC...
There's a very short timeout for editing posts on this forum. You just have to make another post.
I tried editing my post to include my inverter settings... didn't go well... so here they are01 - Utility02 - 60A03 - Generator04 - Saving mode disabl...
About 11500-12000 watts of useable battery which is still 20 hours
@signaturesolarsupport ill call in later today. I’ve walked through the problem a couple times with you guys but no luck. Looks like others are hav...
@joel-brodeur I keep seeing 60W as typical idle/standby consumption for the 3000EHV. @in-offgrid-greenhouse You need to understand a behavior ca...
After looking at the spec a little more, I think the self-consumption of the inverter (while active) might be higher than the 15-70 mentioned before. ...
Don't forget loss do to idle consumption (15W-70W 15 is standby so you are looking at closer to 70) and loss due to efficiency - (94% efficient batter...
I got the answer on another forum. Top line goes to EG4 gen port, middle goes to solar output from Enphase combiner, and bottom goes to main service p...
What AWG are the wires you are using to connect the batteries to the bus bar?