Reply
RE: Enough Batteries or Incorrect Setup

@in-offgrid-greenhouse On that graph, or someplace else in the app, can you identify a point in time (or a few) and let us know what your actual bat...

1 year ago
Reply
RE: Enough Batteries or Incorrect Setup

@in-offgrid-greenhouse OK, then I don't think you have a SOC drift problem - your baseline discharge current of ~6A is high enough to avoid it. F...

1 year ago
Reply
RE: Enough Batteries or Incorrect Setup

@jlankford Load varies between 300W to 500W for some low power heaters in a chicken coop. 1 heating unit stays on all the time, the other unit comes o...

1 year ago
Topic
Forum
Replies: 2
Views: 953
Reply
RE: Whole home backup system with 18Kpv and LL-S rack

@ray I used the battery cables provided in the box, which are 5awg. Some numbers: Max system current: 280 A DC Max current per battery: 47 A DC...

1 year ago
Reply
RE: Enough Batteries or Incorrect Setup

There's a very short timeout for editing posts on this forum. You just have to make another post.

1 year ago
Reply
RE: Enough Batteries or Incorrect Setup

I tried editing my post to include my inverter settings... didn't go well... so here they are01 - Utility02 - 60A03 - Generator04 - Saving mode disabl...

1 year ago
Reply
RE: Enough Batteries or Incorrect Setup

About 11500-12000 watts of useable battery which is still 20 hours

1 year ago
Reply
RE: Another Generator question

@signaturesolarsupport ill call in later today. I’ve walked through the problem a couple times with you guys but no luck. Looks like others are hav...

1 year ago
Forum
Reply
RE: Enough Batteries or Incorrect Setup

@joel-brodeur I keep seeing 60W as typical idle/standby consumption for the 3000EHV. @in-offgrid-greenhouse You need to understand a behavior ca...

1 year ago
Reply
RE: Enough Batteries or Incorrect Setup

After looking at the spec a little more, I think the self-consumption of the inverter (while active) might be higher than the 15-70 mentioned before. ...

1 year ago
Reply
RE: Enough Batteries or Incorrect Setup

Don't forget loss do to idle consumption (15W-70W 15 is standby so you are looking at closer to 70) and loss due to efficiency - (94% efficient batter...

1 year ago
Topic
Replies: 23
Views: 3169
Reply
RE: Wiring Question for EG4 6000 transfer switch for AC coupling off an Enphase combiner box

I got the answer on another forum. Top line goes to EG4 gen port, middle goes to solar output from Enphase combiner, and bottom goes to main service p...

1 year ago
Forum
Reply
RE: Whole home backup system with 18Kpv and LL-S rack

What AWG are the wires you are using to connect the batteries to the bus bar?

1 year ago