Eric, it switched back over off the grid. but, the issue is with the mobile app, it does not correctly set the AC charge parameters. I was able to get...
What is your inverter's serial number or station name? I can take a look at it for you. For the Batteries SOC, you can Top balance them. Charging them...
The batteries reappeared and it's at 25 percent now, but I don't know how to get it to stop using grid bypass. I have it set to only do grid bypass at...
I'm looking for the wire size the terminal can accommodate. I know the recommended is 8 AWG. And you've seen 6 AWG. But, what is the maximum size?
Hi Gang! Thanks for all your comments. I had technicians out to look at it and spoke with several eg4 reps and seems the power is too dirty, they'll i...
@somej Thank you for the pictures! I sent them over to our battery technician. I'll let you know when I get an answer from him. Should be either tomor...
@jp-ouelletteWere you able to get this going?
If the grid isn't connected to the inverter, you can connect the generator to the grid port and enable Micro-Grid mode to prevent it from feeding powe...
Batteries 7-12 are v2 4dip units. The rest are all 6dip v2, v3, or v4.
@eg4eric Here ya go. 8 racks with 6 batteries per rack. The number on each battery corresponds with the number set on that battery's dips. Thank...
8 AWG is what's recommended, but I have seen people use 6 AWGMinute: 12:45