@eric It is a BA dongle which was purchased in July of 2024. How does this get upgraded so the firmware can be updated to enable a complete set of ...
@jlankford I switched to Volt with a set high voltage of 59V since the BMS is set for 58.4(3.65 per cell). What happens is when one cell in each of...
They are on the input to the grid breaker before the 18KPV. I originally had them inside the 18KPV box but was told that can sometimes be noisy so I m...
Right now, my batteries are putting out 435W while my Load is consuming 572W.
@jlankford I agree that is a good idea. Thanks for the feedback!
@jlankford @jlankford great idea looking at the inverter data details. I can see when it happened, at 11:35a and that's what I see when I look at h...
I had changed the setting on the BMS Config page which said 15S for the battery configuration to 16S and that bounced the battery(rebooted) but also s...
It's now exporting 2kw to the grid even though the batteries are at 77%/52.5V. Anyone know which setting will stop it from feeding the grid with batte...
@jlankford it's only out of context when it considered to be talking about the cells/batteries instead of the system(BMS+batteries) since it is the BM...
@jlankford I believe the post by @signaturesolarjess was more of a 'battery system' symptom when the BMS doesn't count the coulomb correctly and the S...
My batteries are the Basengreen DIY 314aH/16.2kWh with an active 2A balancer and I originally assembled and connected 2 packs together and I ran them ...
@ron I don't know what battery cells you have but the manufacturer of my cells, EVE, state that the min low voltage is 40V(2.50V each) on the pack of ...