RE: 6000xp bug in charge controller setpoint voltages with open loop

these settings did not work by the way.... charge behavior showed that system ignored the EQ setting, and just stuck to a CV=54.5..... which results i...

2 years ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

@jarrett , thanks for followup... if and when a patch is ready to test, I am more than willing to be a beta tester and report results. The goal of cou...

2 years ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

@jarrett , great, I'd appreciate that. What I am looking for is the ability to set inverter charge setpoints such that I get a proper CC/CV charge cur...

2 years ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

tried a few more things, which @jarrett may want to pass along to developers. I have set: Batt type=lead-acid Veq= 56.5, days=1, duration=1 hr (mi...

2 years ago
Forum
Reply
RE: 6000 XP set solar charge limit?

@jpangburn ... not pointless to be concerned, but better to be educated. using LFP in cars is far different than solar; mostly because of the charge c...

2 years ago
Forum
Reply
RE: 6000 XP set solar charge limit?

@jpangburn if you are running with closed-loop rj485, and have successful communication, then setting battery type to Li (lifepower4) lets the batteri...

2 years ago
Forum
Reply
RE: 6000 XP set solar charge limit?

@jared , you gave an incorrect and incomplete response.... a. LFP charge curve *should* bulk charge to 56.2, and float at 53.5-54.0 for best results...

2 years ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

@jarrett , I'd be happy to be a beta-site tester at one of my client sites if there is a patch available that can be installed with the remote update ...

2 years ago
Forum
Reply
RE: 6000 XP set solar charge limit?

running off-grid, you really do want to charge to 100% every day possible to start the night with full batteries. A 'correct' charge curve for LFP bat...

2 years ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

Still, no response or followup ? very disappointed in EG4 at this point. I'm going to have to evaluate other inverters, or add external charge control...

2 years ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

@jarrett .... kinda expecting an update by now. It's pretty serious to not be able to set correct bulk/float voltages. I would hope that the 6000xp ch...

2 years ago
Forum
Reply
RE: 6000xp bug in charge controller setpoint voltages with open loop

@jarrett , yes we had emailed back and forth several times.... This new forum will be a decent way to track open bugs, and let people know when patch ...

2 years ago