42 is the max that setting #11 allows me to enter. It says cut off, rather than eod. Is this the same thing?
@eric The battery screen doesn't light up at all. Neither do the bars indicating charge.
@scottmr808 For the WallMount batteries, the Lithium type will be 1 for all the inverters. I did see that you were able to change it. Has your client ...
@scottmr808 Where are you seeing this protection mode? Are you using BMS Tools?
Just curious, could you AC couple the 6000xps to the 18Kpv?
The 18kPv and the 6000XP cannot be paralleled together. To have 2 or more inverters communicating, they would need to be the same (Model) inverters.
Further observations Had the load up to 7800 watts. The battery was running over 7K watts and no warning 28. So now I’m wondering if this “System D...
I’m sorry you’re experiencing this issue. Does the battery screen turn on, but the battery fails to fully boot up? Or does it not turn on at all?
Here are some photos I just took using the junctions directly on the inverter itself. The 8.8 is Amps. 44.9 is the Volts. Here is my screen as w...
How many volts are you getting on the inverter on the PV input?With those panels you should be getting about 200V of PV.There is firmware available, b...
Hi, friends! I’ve gathered some of the highly informative pages for anyone interested in online casinos. Whether you're an experienced player wantin...
I've updated to the latest firmware (ccaa-190D0E) last week and can confirm it's still occasionally happening. I just had it happen this morning, and ...
@zali I don't have a GB, so can't help you there.