@coolrunnings ...can't edit my previous post. I just saw your other post about the Cerbo... So without a BMS input, I'm curious how the 18K deter...
@coolrunnings Cool. I would trust everything you listed except the EG4 screen. My system, consisting of one 18Kpv and six LL-S rack units, can cons...
@jlankford Measuring the battery current with an ammeter with no PV on, as well as a shunt for the Victron Cerbo GX. Plus the EG4 screen shows 0 watts...
@jwmarshall Are you saying that Signature Solar is replacing ten 18Kpv units because of a parallel phase error that only started after a firmware u...
@coolrunnings Thanks for sharing the solution here. Keep in mind the batteries won't register any current unless it is above some shunt measureme...
I made a separate post about how I solved this, but it is apparently stuck in moderation hell, so maybe I can get the word out here. This problem seem...
New to group/EG4...Installed 6000XP,nice setup,the usual non clarity of simple instructions to start and program.I'm 70 and not into apps,etc.I use my...
It discharges from 100 to 99, then it charges the batteries from 99 to 100(SOC). This is the cycle that its stuck in.
I have 2 strings of 6 (535W) panels each. Each string provides about 3kW at about 240-250V and are connected to PV1 and PV2. The panels, which are a...
Just for clarity my battery pack is using a single 100 amp bms that has active balancing with 14 3.7volt nominal cells in series. This is no different...
@bobro Do you have the wifi dongle setup to be able to use the website monitoring? There are a lot of setting and it can be easy to missing going thro...
Hi Jared thanks for responding. I did finally talk to someone at eg4 on phone and he also explained the three settings me in #6, so I did set the iac ...
System went down to 99% and now its charging the batteries again. Start Shaving SOC 1%...what should this be set at?