@joel-brodeur all my readings are taken with a amp clamp.
@pawnee I don't see anything wrong with the wiring. It was working fine 9 batteries? Just curious, have you tried an amp clamp to see if it actuall...
@eric I thought so. The options to update in the EG4 app don't show 12KPV. And I just downloaded the firmware again from the 12KPV inverter page and ...
@joel-brodeur Yes last 3 of the 12. It's pretty strange. When PV or discharge is low, they all pull the same amps. When PV or discharge is high the ne...
@eric Can the 600xp do both at the same time? Can it convert generator AC to battery DC and also invert battery DC to load AC.
@pawnee If I remember your OP correctly, the three new V2's are just filling out your second rack? The original setup was charging all batteries cor...
@eric 2 EG4 battery racks connected to 18k with 2, 3/0 cables for positive and 2, 3/0 negative. The 2 racks are connected by a 4/0 positive and a 4...
Boy! Talk about being LUCKY! This past Tuesday, as advertised, I put my half of the Income tax return (plus some rat-hole $$ - aka savings) ...
Understanding that this is not your fault: It still HURTS like hell. on Tuesday I paid this (i could feel it in the "air"): This Morning: ...
@eric This is how it’s working now. Charge voltage is reached and the generator stops charging and powering the house. Batteries take over no probl...
@eric If anything else might help, please let me know.
You are still getting it when it switches to generator and when it switches from genrator to batteries?