@brokenpointjoe The history of generators and inverters charging batteries is an old problematic issue. Inverters seem to have a hard time "walking an...
@ron Perhaps, but Signature Solar and EG4 marketed these systems to people with the understanding that a generator would work directly wired to the ge...
@jared I searched EG4's online resources and downloaded a generator page state the minimum generator size was 4kW. Just saying there is an inconsist...
@jlankford I would assume that it knows how many AC amps it's producing to determine the power output. Does it not know how many DC amps are coming in...
@coolrunnings ...can't edit my previous post. I just saw your other post about the Cerbo... So without a BMS input, I'm curious how the 18K deter...
@coolrunnings Cool. I would trust everything you listed except the EG4 screen. My system, consisting of one 18Kpv and six LL-S rack units, can cons...
@jlankford Measuring the battery current with an ammeter with no PV on, as well as a shunt for the Victron Cerbo GX. Plus the EG4 screen shows 0 watts...
@jwmarshall Are you saying that Signature Solar is replacing ten 18Kpv units because of a parallel phase error that only started after a firmware u...