Would you be able to DM me the serial number for the inverter? I would like to take a look.
I recommend this guide, even though it's listed for the BJxxxx, BGxxxx, and BExxxx dongles—it should still be useful: EG4 Wifi Dongle Troubleshooting ...
I recommend continuing to charge with the Chargeverter up to 56.2V. Although the BMS won’t trigger overvoltage protection until a cell reaches 3.8V, 5...
@pawnee Which firmware version is installed on the LifePower4 V2? In my opinion, 0% would not be 47v. However, it would be very close.
@dlwittsr If the CAN protocol is set to EG4/LUX, the BMS communication will remain active. I’d suggest switching the RS485 protocol on the master batt...
Were there any error codes reported with this? Also, if you are able to DM the serial number for the inverter, I can take a look at it on the monitori...
We are still investigating the bug not allowing the 6000XP to equalize while in lead-acid. However, this solution from another thread may work as a qu...
The best solution would be to run the PV ground to the earth ground installed at the home grounding rod.
@umar I do not have documentation that covers this. However, I will be updating this thread as soon as I receive an answer.
Page 33 of the manual has a few details going over each button on the remote control.
The firmware update is not needed, but there are improvements to the cycle count logic.That is the correct cable for the RS232 update. The RS232 is re...
What is the discharge current limit set to? Also, what size is the battery bank? With two inverters, the minimum this should be set to prevent EPS ...
@benl697 looking into this now.
The closed loop vs open loop white paper on our website might be worth a read as well.