I recommend setting the PV Charge Priority to 100% or your desired SOC and configuring the battery priority timing accordingly. This setup allows the ...
The CTs are mislabeled. If you'd like them oriented correctly, I can adjust the CT settings in the inverter, or you can leave them as they are current...
I've noticed some CTs have been mislabeled from the factory. Could you share screenshots of the readings along with the CTs' orientation? I can verify...
I believe this to be the normal/idle consumption of the 18kPV.
I do not see any reported outages. I would recommend testing different channel numbers on your router's 2.4GHz band. Local interference on the current...
Would you be able to send me a DM of the serial number for the inverter and I can take a look at it.
I don't believe the firmware for the 24v Lifepower4 V1 is listed. However, let me see what I can find.
@idee if you don't mind sending me a DM with the data or serial number of the inverter, I would definitely like to take a look.
What protocol is configured on the batteries, and which lithium brand is selected on the inverter? Based on the screenshot, these appear to be Indoor ...
Feel free to DM your serial number and I can verify that it is correctly configured. However, this sounds normal for on-grid use.
I recommend reviewing our white paper on closed-loop versus open-loop systems for a detailed explanation. Personally, I prefer the BMS communication p...
What firmware version is currently installed on both the battery and the inverter? Also, which lithium brand is selected on the inverter, and what pro...
The input for Chargeverter only allows for VAC.
With the discharge curve of the battery, the voltage range from 52V to 50V typically corresponds to an 80% to 20% state of SOC. However, since voltage...
I will need to consult with our R&D team for this. Once I have the information, I’ll share it in the thread.