Any news on this? JB
@jlankford FWIW I agree that the Numbers and "reasoning" are not right for LFP batteries. I think a better way to explain would be that when bat...
@in-offgrid-greenhouse You might have a look at the following thread: @signaturesolarjess Discussing how to "Reset" SOC"
@in-offgrid-greenhouse Hmmm, that is a head scratcher. Based on that you are only "Self-Consuming" around 20Watts. Offhand the only thing I can think...
@in-offgrid-greenhouse On that graph, or someplace else in the app, can you identify a point in time (or a few) and let us know what your actual bat...
After looking at the spec a little more, I think the self-consumption of the inverter (while active) might be higher than the 15-70 mentioned before. ...
Don't forget loss do to idle consumption (15W-70W 15 is standby so you are looking at closer to 70) and loss due to efficiency - (94% efficient batter...
@signaturesolarsupport It would be great to hear something on this as it is also an issue with the 6000xp. It is almost like when the gen gets the shu...
If you are using closed loop communications between the Batteries and the inverter you should be able to see the Bat count on the right side of the we...
Do you have a PV string(s) connected to that inverter? If so, use your disconnect and remove that string(s) from the inverter. Clear the error and s...
@m-piedlourde I am glad it is working but that is kind of strange. 🤔
Have you been able to connect the phone app to see if it is showing any warnings or alerts? JB
@pawnee I haven't seen @jared around the forum much but maybe @eric will chime in? JB
@pawnee I was browsing the 18K manual and came across this: regarding seamless switch. Didn't find much info on it, maybe the folks at SS could e...
Looks excellent! Great work. JB