@Joel-brodeur @pawnee Could you both send me a private message with your inverter's serial number? I'd like to review some data and verify that everyt...
@hanzi When you measured the PV input at the inverter, were the batteries still connected? If so, try disconnecting the battery power and measuring ag...
Sorry for the late response! I try to answer as soon as possible! Yes, this makes sense, Since the inverter must convert AC to DC to charge the batter...
Is the "Grid Boss Enable" option Enabled?This would be located in the settings on the top right under "Working Mode" and then under "Advanced settings...
Thank you! I'll forward this shoutout to Rodolfo!
Still trying to get resolution from Tier 2 support. After hooking up the parallel cables correctly and doing the sync, the gridboss is just showing th...
@joel-brodeur It was just a simple fix! Charge ahead!
Great news and now I feel stupid. I was going to ask about that, but I figured since you had been powering loads you had the EPS on. Would you mind...
@joel-brodeur @eric @jlankford Okay! Problem solved! The solution is a simple one. In order for the AC to charge the EPS switch needs to be ...
Okay! Problem solved! The solution is a simple one. In order for the AC to charge the EPS switch needs to be in the ON position with the load break...
I see the UL 9540 certificates of compliance have been posted and the site was updated on 1/29. Thank you!
@eric @joel-brodeur Thank you for the continued feedback! It is very helpful. I did sent a note to my electrician about adding the safeguard to...
@jlankford I agree that an interlock should be installed but for now it is manual switch of the breaker.