Yes. I can do that during the day tomorrow, 4/17 during the day EST. What time works for you?
The FlexBoss21 is designed to work specifically with the GridBoss and does not include an input for a generator. To have communication between a gener...
1. True 120V/240V split phase2. Make sure you have 120V on L1 and 120V on L2. For the settings you need to make sure it is set to 120V/240V which shou...
True 240V. With multiple inverters make sure all L1's and L2's are on opposite sides of the Grid panel
Adding to the mix, I set the system to "Charge battery last" and the problem was gone. I also disconnected the Grid, and the problem was still there, ...
Hi @eric, can you address my question which is still pending as needs "Approval"?
Are you able to run quick charge again so we can monitor the system while the charging is happening, and we can look at the settings to see what exact...
I was able to look at your settings and it looks like you have the Charge Last setting enabled. This would cause the inverter to sell back to grid and...
You would connect the CTs on Line 1 and Line 2 between your meter and service panel with the arrows pointing towards the inverter and you would plug i...
Also note, the issue is recurring.