Adding more context. I disabled the AC Charge Mode removing it from my working mode settings. This left only Peak Shaving Mode and the problem persis...
Reading the literature, it seems that by only using the grid during a PV Charge Priority window, and not allowing off grid mode to go from Grid Use ba...
I would expect the time window to take over for allowing an AC charge within that window. I did not expect it to switch away from self consumption to...
The question is why doesn't the Inverter use the battery when set to Time+SOC/Volt but it will use it when set to SOC/Volt. Setting to Time+SOC/Volt p...
So I have narrowed this down to a logic problem in the inverter related to working modes. One with the AC Charge mode time window and the other when t...
Off Grid Mode On after Restart Off Grid Mode Off
It did it again this morning. Battery was depleted down to 12% (battery cutoff is at 10% which had happened), in Off Grid Mode, EPS relays were off a...
I have a single Eg4 15k indoor battery.
It did it again today but I couldn't leave it that way and miss another day of charging. It seems like in Off Grid Mode, once the battery gets down to...
So it finally switched over to EPS on its own at 1:01pm then back off and back on again at 1:09pm when if finally stayed on and started charging the b...
So this morning it appears to be doing it again. When the loads turned on, solar immediately jumped 2500watts to meet the load but had not been using ...
Of course, this morning it did not seem to do it. So its intermittent.
For reference, below illustrated a typical load/charge scenario where it worked correctly. My loads are automated so they are always the same and the...