Reply
RE: Will the grid pass through the inverter if the inverter fails

No. My system is a whole-house backup configuration. Main disconnect and transfer switch are before the 18Kpv. Main dist panel is after the 18K. G-N b...

6 months ago
Forum
Reply
RE: Will the grid pass through the inverter if the inverter fails

@jlankford will the transfer switch need to also transfer the neutral and ground? Main panel is bonded before the inverter and dist panel after invert...

6 months ago
Forum
Topic
Reply
RE: LiFePo04 v2 Serial number

I had to come back quickly, I found that each box the batteries came in has a sticker of the SN. DD

6 months ago
Forum
Topic
Replies: 4
Views: 382
Reply
RE: LiFePo04 v2 Serial number

@Jared I also asked to verify my registration to confirm the numbers. However, after 2 months, I have received no reply on this forum.

6 months ago
Forum
Topic
Replies: 1
Views: 345
Reply
Reply
RE: Another dongle question

Yes, we do offer an ethernet dongle.Ethernet Adapter - EG4 Electronics

6 months ago
Reply
RE: Generator charging problems

Did you update the LCD firmware as well?

6 months ago
Reply
RE: Sequence of operation for modes

You can find the working modes in section 12.3 of the manual. The link is attached below. EG4-12000XP-Manual.pdf

6 months ago
Forum
Reply
RE: Need help configuring 2 paralleled 6000xp with 2 different batteries

@highstone That's correct! each inverter will handle its own battery but both inverters' will still work together to power the loads.

6 months ago
Forum
Reply
RE: RSD?

@eg4eric Thank you

6 months ago
Forum
Reply
RE: Will the grid pass through the inverter if the inverter fails

The 18Kpv does NOT pass through unless the inverter is running. The default state for the pass through relays is open, not closed. The inverter softwa...

6 months ago
Forum