@kw5kw very good. Thanks
@joel-brodeur - I connected the AC input from the inverter to my house's grid-tied panel, which has a neutral-ground (NG) bond (with No AC loads conne...
Complicated answer. Could the equipment you have provide backup to a house running moderate loads for while - yes. As others have indicated it wou...
What do you have for HVAC, dryer, water heater, stove and oven, out buildings, well pumps. Anything else that draws a lot of power. 240V stuff? I'm ...
Ok so are you using Solar assistant to control the time of use? or is this all done via the 6000xp? i was hoping Solar assistant can control the...
I think it all depends on the power consumption of your house. I have the 6000xp set up for our off-grid cabin with 5, 48-volt, 100h batteries. It eas...
@jlankford Yes, sorted the generator issues. I gave up on trying to sort out the battery balancing issues here, since there was little response from E...
@joel-brodeur - Interesting. You'd think there'd be blocking diodes or MOSFETs protecting the inputs to stop any current backflow. Both would cause sm...
@hanzi I had similar experience while commissioning a 6000XP, as soon I got an Earth Ground and a NG ground at the panel (not the programmable NG bond...
@joel-brodeur - I have been testing the inputs with correct polarity (red + / black -), and reversing the polarity does result in a negative DC voltag...
PARDON me, I misspoke... Parallel it is. they do they are they do I see that now. I do not export anything to the grid. I just wa...
I had the same problems and more when adding V2's to my V1's. V2's will have to be on first in the rack to communicate properly. You will also most li...
I should clarify, What is a 2 x Rotary? Is that an inverter type of compressor or not?