@ray Where did you see or hear about the Self-Balancing via BMS? I just want to make sure we clarify any confusion.
@ianscott that's a direct connect to the batteries and then you have to make sure the inverter and chargeverter play nice together while solar and gen...
@michaelahess Once you change the inverter to Lead acid, the SOC parameters will not matter since it's going based off of voltage. So, you will need t...
@ianscott That is the best solution!
Do I keep the SOC settings for charging and discharging, just up the absorb to 57?
I've been trying to keep it from 100 to 20, but it regularly goes to 8-10, even though I have the inverter cutoff set to 20%. It may need a calibratio...
I reached out to the retailer in early September, and they have been unable to provide a replacement unit as they are on "backorder". Is it possible ...
To recalibrate the battery, you’ll need to charge it to 57V using either a 48V charger or the inverter set to Lead Acid mode.Are you regularly chargin...
Yes, the 2 wore Start/Stop will work when Micro-Grid is enabled.
Yes, that's exactly what I do. I use a small 2,000 watt 120VAC generator through a Chargeverter. This is a manual start/stop solution and bat...
We are pretty sure the initial "proposed" is not good, we have modified it.
Your batteries are all balanced, indicated by the voltages being the same, and guaranteed by the fact that you have them all tied together in...