[Closed] Previous Changes

1 Posts
1 Users
0 Reactions
81 Views
Jared
(@jared)
Posts: 150
Online Support Moderator
Topic starter
 

EG4_EAAB-1A1A

2024-04-22
  • Same as fAAB-1A1A, changes based on the FAAB-1919.
  • 1.Add 2 minutes of Warmup to the generator microgrid mode.
  • 2. Add split phase voltage overvoltage and undervoltage protection for US models.
  • 3. Improvement, keep off-grid state when countdown to connect to on-grid mode. At the end of the countdown, it will quickly switch from off grid to on-grid mode.
  • 4. Improve load calculation in three-phase parallel and on-grid mode.
  • 5. Fix the issue of using Grid AC to charge even when SOC/Volt reaches Stop AC Charge SOC/Volt when AC Couple and AC Charge are enabled.
  • 6. Optimize AC Couple power display.
  • 7. Fix the issue of the original AC Couple power not being able to reset to zero when the AC Couple is disconnected from the grid and there is no grid power.
  • 8. Update PR-LUMA grid regulations parameters.
  • 9. Update register information for "Permit Service".

EG4_EAAB-1919

2024-03-18
  • Changes based on the FAAB-1818
  • 1.Corrected the sampling of NPE connection.
  • 2. Logic optimization: When the battery SOC/Voltage is lower than "Start generator charge SOC/VOLT" limit, the dry contact turns on, and only when there is generator input, the inverter enters generator charge mode.
  • 3. Optimized the control logic for the following scenario: When the PV power is sufficient, but grid sell back is not allowed and there is no load compensation requirement, once battery is fully charged, BUS over voltage issue happens.

EG4_EAAB-1818

2024-02-26
  • (Same as fAAB-1818)based on FAAB-1616 and FAAB-1717
  • 1.New feature— Parallel Setting Data Sync, synchronize the settings of primary and subordinate inverters.
  • 2.New feature— Gen Boost, which enables the PV and battery to work with the generator together when the generator power is insufficient to handle the load.
  • 3.New feature— Battery Backup Mode. When enabled, the batteries will stay at the appointed SOC (default 100% SOC) unless there is no grid or grid abnormality or no generator port input.
  • 4.New feature—N PE relay control
  • 5.New feature—Gen overload alarm, if the generator power is greater than GenRatedPower+500w for 1 minute, an alarm prompt will appear.
  • 6.Newly added—127/220V Grid Type. When set Grid Type to 120/208V, set EPS Voltage to 220V, the grid protection rules can be automatically adapted.
  • 7.Newly added—Grid Peak-Shaving Power 2 kW, effective for corresponding time period 2.
  • 8.Newly added—EPS overload recovery time is upload.
  • 9.Newly added—Generator Cool-Down Time (Min) setting. After the generator is charged to the cut-off voltage, the inverter will not switch back to the generator for power supply unless it has not been shut down before exceeding the cooldown set time.
  • 10.Improvment—Optimization of generator related logic. When manually starting the generator, as long as the GeneratorChargeEndSOC/Volt setting is not reached, it can still be charged. After stopping charging at GeneratorChargeEndSOC/Volt, there is a delay of 5 minutes for allowing to recharge to prevent repeated switching.
  • 11. Improvement—Optimization of Quick charge. The inverter will automatically change its settings and use the AC charge function for the next one hour. After the charge is completed, the settings will be restored.
  • 12. Improvement—The range of AC Couple Start/End Volt/SOC are enlarged.
  • 13. Improvement—AC Couple can be used normally, when Micro grid enabled but generator is off.
  • 14. Improvement—Adjust the range of lead-acid battery Ah settings from 50Ah to 5000Ah.The triggering current entering float charge mode can be changed (defaults to 0.01C).
  • 15. Improvement—Surge protection supports EPS output by1.35 times rated power for 1 minute.
  • 16. Improvement—Balanced load during parallel and on-grid mode.
  • 17. Change—The Share Battery function in the US version is enabled by default.
  • 18. Problem fixing—Fixing the issue of generator cannot be able to shut down after being started up by Quick Gen start. Generator will be automatically shuts down after 20 minutes of startup.

EG4_EAAB-1717

2024-01-18
  • Changes log (Same as fAAB-1717)based on FAAB-1616
  • 1. New feature: On-grid load balance and PV Sell for parallel system
  • 2. New feature: Parallel settings synchronization
  • 3. Flicker optimization: Voltage drop when heavy load start
  • 4. Optimization for generator application, such as transfer time, warm up, cool down, exercise, and quick start&stop remotely.
  • 5. Issue fixed: Generator End volt/SOC setting not work
  • 6. Bug fixed: Cannot exit EPS mode when RSD active
  • 7. Raise default value of start&stop volt/SOC for AC Couple, if PV inverter does not derate power at over frequency, customer can set lower value to disconnect it by generator relay
  • 8. Enable Share Battery Function by default for US version

EG4_EAAB-1616

2023-10-20
  • Changes log (Same as fAAB-1616)based on FAAB-1312.
  • 1. Optimization on frequency shifting for AC couple function has been done.
  • 2. Optimization on Zero export function: Stop frequently switching between PV charge +Grid on and PV+Battery grid on modes.
  • 3. 3phase (208Vac/120Vac)parallel solution has been supported: 2 *208V 3phase parallel and 3 *208V 3phase parallel are supported.
  • 4. Optimization on EPS transfer time has been done.
  • 5. RSD active signal to BMS has been added: Battery needs to support the respond to RSD demand too.
  • 6. The setting range of Generator rated power has been changed to 255kW max and 1kW min.
  • 7. Logics optimization: Once "Fast zero export " function is enabled, " Grid sell back " function won't take effect.
  • 8. Refined parameter adjustments for Battery control: On-Grid cut off VOLT form(40-52V)to(40-56V); AC Charge Start Volt from(38.5V-52V)to(40-57V); AC Charge End Volt from(48V-59V)to(42-59V); Gen Charge Start Volt from(40V-59V)to(40-57V);Gen Charge End Volt from(40V-59V)to(42-59V),AC Couple Start Volt from(start-59V)to(42-59V).
  • 9. New Feature for LCD display: "Connect in xxxs " for the waiting time to on-grid mode will be showed at the top line of the home page.
  • 10. Logics optimization on Generator dry contact control: Warming up the generator for 2 minutes before entering charge mode and cooling down the generator for 2 minutes before cutting it off.
  • 11. Optimization on voltage drop of EPS output while connecting or disconnecting with heavy load has been done.
  • 12. Logics adjustment: When forced discharge function is enabled, AC coupling power will prioritize to export to grid instead of going to AC charge mode.
  • 13. Logics adjustment: When PV energy is weak, to prevent switching PV grid on mode frequently with high frequency relay clicking noise, the time delay to enter another check changes to 2 seconds.
  • 14. New Feature: System charge end SOC:0-255%, VOLT :40-59V.

EG4_EAAB-1312

2023-08-16
  • Changes log (Same as fAAB-1312)based on FAAB-1010.
  • 1. Optimized surge power and addressed voltage drop concerns when operating in EPS mode.
  • 2. "PV sell to grid" function is supported; Note that it's not yet available for parallel systems.
  • 3. Refined parameter adjustments for LUMA Grid regulation.
  • 4. With firmware version FAAB-1010, enabling the "run without grid" function won't activate generator dry contact logic.
  • 5. Resolved EPS overload triggers from both total EPS voltage and split-phase voltage.
  • 6. Improved control to prevent " BUS voltage High " issue when operating in AC couple mode.
  • 7. Enabled RSD control synchronization in parallel systems.
  • 8. Implemented "strict zero export "; When PV and battery energy suffice for loads, the inverter won't exchange energy with the utility grid.
  • 9. Modified AC coupling input recognition, treating it as PV input with equivalent priority as integrated PV power.
  • 10. In previous firmware
  • FAAB-1010
  • and with fast zero export active, the inverter won't switch to PV charge mode when battery energy is low.
  • 11. Improved surge capacity: For power levels between Pn and 1.16Pn, 10 minutes; and between 1.16Pn and 1.3*Pn, 5 minutes.
  • 12.Default settings for Lead Acid mode include a charge voltage of 55V and charge/discharge current limitation of 0.5C.
  • 13. Enhanced generator quick start functionality.

EG4_EAAB-1010

2023-06-30
  • Changes log (Same as fAAB-1010/ eAAB-1010/EAAB-1010)based on FAAB-0D0E.
  • 1. Enlarged the grid sell back power limitation, if power limitation is high than 200%, then real limitation will be 1000% max.
  • 2. Peak-shaving logic optimization.
  • 3. Fortress battery protocol optimization: working in lead-acid mode where is communication failure issue.
  • 4. AC Charge according to SOC or VOLT could be supported in this firmware version.
  • 5. Octopus charge function is supported.
  • 6. To avoid relays clicking on and off frequently due to grid fluctuation, a return value has been added in this firmware version.
  • 7. Hina battery protocol is supported in this firmware version.
  • 8. Grid regulation changes: Hawaii changed to HECO, added KIUC grid regulation.
  • 9. Battery capacity could be showed in the LCD display.
  • 10. Optimization on AC coupling function: AC charge and battery discharge will be seamless switching way.
  • 11. Fans control logic optimization to reduce fans noise

EG4_EAAB-0D0E

2023-05-12
  • Changes log (Same as fAAB-0D0E/ eAAB-0D0E/EAAB-0D0E)based on FAAB-0C0D
  • 1. Fixed the logic issue when PV energy is low, the inverter would fail to switch work mode from PV charge to battery discharge
  • 2. Optimized charge logic of AC coupling input and maximize the use of AC coupling charge
  • 3.Optimized the logic of charge limit in AC charge mode.

EG4_EAAB-0C0D

2023-04-13
  • Changes log (Same as fAAB-0C0D/ eAAB-0C0D/EAAB-0C0D)based on FAAB-0C0C
  • 1. Adjusted Control logic of Aging test in Luxpower factory

EG4_EAAB-0C0C

2023-04-03
  • Changes log (Same as fAAB-0C0C/ eAAB-0C0C/EAAB-0C0C)based on FAAB-0B0B
  • 1. Adjusted Control logic of Aging test in Luxpower factory

EG4_EAAB-0B0B

2023-03-28
  • Changes log (Same as fAAB-0B0B/ eAAB-0B0B/EAAB-0B0B)based on FAAB-0A0A
  • 1.CT direction could be corrected remotely and individually in 3phase parallel system.
  • 2.Non battery shared mode, current limitation will depend on individual battery banks
  • 3.Fixed discharge configuration in LCD: in previous version, discharge power needs to be configured twice to take effect, and this bug has been fixed in new version.
  • 4.Fixed discharge configuration in LCD: in previous version, discharge power needs to be configured twice to take effect, and this bug has been fixed in new version.
  • 5.Modified Hawaii Grid regulation: QV curve
 
Posted : October 11, 2024 7:09 pm