I have a client 6000xp running off-grid and charging LFP with firmware ccaa-191011.... almost correctly, but has a bug which turns off AC-out to loads for 20 seconds or so after hitting vBulk, and sometimes bounces between vFloat and vBulk a couple times before settling to float.

Can anyone verify that ccaa-1c1212 fixes this and does not introduce any other problems ?

secondly.... since this site is off-grid with no AC-in available... the wifi will be powered off if the inverter is in standby mode. Will I be able to do this update for my remote client without going on-site myself to initiate the update and re-start inverter ? I am unclear on how I can do a remote update if their wifi modem is turned off when inverter is in standby and ACout to Loads is turned off.

Does the download of the update occur first, while inverter is running loads ? Does the inverter sequence thru upload and restart without local power for the modem? .... will it work if I do it during the day when PV power is available, or do I need to go out to the site with a dedicated power source for the modem during the update and restart ?


 
Posted : February 8, 2026 9:34 pm
(@dtbaker61)
Posts: 153
Estimable Member
Topic starter
 

I did update a client to ccaa-1c1212 , and open-loop charge control by voltage does now  appear to work almost cceptably. System charges to bulk, ends charge, and drops to float.... all good as long as incoming PV > Load. However, if Load >PV, vBatt will drop -1.0v below float, and re-bulk to end-of-charge, stop charge, and drop back to float -1 and cycle again.

this can result is some weird looking

2026 03 25 shows bad re bulk cycle

battery voltage in the afternoons. better than holding at bulk, but *should* cycle only up to Float, not Bulk voltage

 


 
Posted : March 25, 2026 2:34 pm