I wanted a place in this Forum for EG4 users with AC coupled PV systems to compare notes. If this discussion belongs elsewhere, somebody let me know and I'll try again.
I have 20 Panasonic Evervolt panels with Enpase IQ8 microinverters connected to an EG4 15K inverter and a outdoor wallmount 280AH battery - installed indoors. The system was commissioned only a few weeks ago, so I've not had much experience with it. A couple of oddities I'm wondering about are:
Has anybody else experienced either of these situations? Is your AC Coupled system running perfectly? Or if not, what's up?
Tristan again. Since my last post, I've learned from EG4 support that having the power flow image show power going to the EPS icon when off grid is normal - even when you don't have an EPS. Coulda fooled me.
But I'm still having trouble getting the charging to work as I think it should. Could anybody clarify the role of the various charging parameters for on grid and off grid operation?:
On my system, when on grid, it still looks like the start values are ignored. That's OK, but I would like to at least understand how the Limit and Stop values are selected for both on and off grid. I suspect this would be useful for other AC Coupled users as well.
The System Charge SOC limit refers to the maximum allowable state of charge for the system. The Start and Stop AC Charge SOC settings define when the AC input will begin charging the batteries and when it will stop.
Below is an example using 80% start and 99% end SOC:
When Battery Capacity is Higher than Start SOC (80%)
When SOC Reaches 100%
When PV System's Energy Production is Insufficient
When Total PV Energy Production Exceeds Battery Charging and Load Requirements
Also, if frequency shifting is needed, I would recommend having the AC couple start SOC set in the range of 95-99% with the ending SOC set to 100%.
Thanks Jared. But just to clarify:
In example 1 where you wrote "AC coupling will not operate." I think you meant "AC charging will not operate". Same thing for example 2.
And I think both of these examples refer to the AC Charge Start and Stop that are included in the "Charging" section of settings on the Monitor web site. I'm guessing that these settings can only apply when GRID AC is available, right? The fact that solar AC is available isn't relevant.
On my system, I have the System Charge SOC limit set to 85%, the AC Charge Start at 75%, and the Stop at 85%. The system starts charging at 80% and charges up to the 85% stopping point. It ignores the 75% Start setting. That's why I'm a bit confused about how these setting are supposed to work.
But the rest of my original question was how the AC Couple Start (and Stop) SOC work. These are the settings in the AC Couple section of the Monitor website. Do these settings only apply ONLY when off grid, and when there is excess solar AC available?
In keeping with your recommendation, and my preference not to fully charge the battery while it's not being used, I have the Stop set at 85% and the Start at 84%. Is that OK?
Were there to be an exetended grid outage, I'd raise them to the 99% and 100% that is recommended.