Feedback on FlexBOSS21 + FlexBOSS18 Stringing Plan (47 × JA-Solar 440W)

1 Posts
1 Users
0 Reactions
2 Views
 mray
(@mray)
New Member
Joined: 23 hours ago
Posts: 1
Topic starter  

Hello everyone,

I’m planning to install 47 JA-Solar JAM54D41 440W panels (Vmp ≈ 32.47 V, Voc ≈ 38.9 V, Imp ≈ 13.55 A).

At first, I thought a single FlexBOSS21 could handle the full array since we’d be under the 21 kW PV limit. After reviewing the MPPT current limits, I realized it isn’t possible to safely distribute all 47 panels across its 3 MPPT inputs.

To stay within spec, I’m planning to add a FlexBOSS18 and split the array like this:

  • FlexBOSS21: 31 panels → 3 strings (11 / 10 / 10)

  • FlexBOSS18: 16 panels → 2 strings (8 / 8)

Both inverters will be connected to three EG4 Wallmount indoor batteries wired in parallel.

Does anyone see any issues with this setup? Any suggestions for improvements or alternative approaches?