Question 12000XP Off-grid with 120v generator.

4 Posts
4 Users
0 Reactions
430 Views
Posts: 1
Topic starter
(@ionstorm66)
New Member
Joined: 2 months ago

I have a 6.5kw 120v 50a generator I would like to use with my 12000XP. I don't thing chargverters can be paralleled thus only 2500w output, so my question is there anyway to use the generator or grid input on the 12000XP to charge the batteries off the 120v generator?


3 Replies
EG4 Eric
Posts: 1215
Admin
(@eg4eric)
EG4 Online Support
Joined: 2 years ago

You will need a 240V generator to connect it to the inverter and charge the batteries. You can use a 120V generator with the Chargeverter, but it will be limited to a maximum charging current of 45A.


Reply
1 Reply
(@krzysiek_kta)
Joined: 2 years ago

Estimable Member
Posts: 104

@ionstorm66

 
Another option to above is to use autotransformer 120/240V as the intermediary between the 120v Gen and the Inverter. 
 
e.g. Victron-Energy-Autotransformer-120-240V-32A
 
I installed  one and the setup works for me - it converts any 110v source to 240V and can power my GEN port
 
Ther est can be set-up in gen settings of the inverter.
 
Just my 5 cents
 
Brgds
 
K
 
 
 


Reply
Posts: 148
(@dtbaker61)
Estimable Member
Joined: 2 years ago

I have not had good luck charging directly with any "smallish/cheaper" generators even if they are 120/240. The EG4 inverters seem to be fairly picky and require a very clean sine wave and stable voltage. This means you might as well use a cheap generator and a chargeverter, or any similar 120vAC->48vDC charger direct to battery to get enough charge to get thru the night.

 

I typically tell off-grid clients to get in the habit of checking battery voltage at dusk before cooking dinner.... and if SOC% is <50%, then fire up the Genny, and run it until bedtime.