3 x 300EHV in paral...
Question 3 x 300EHV in parallel
(@philip14505)
I want to pre-run AC input for future inverters as well as AC output. I am a little confused by the instructions for adding a 2nd and 3rd 3000EHV in parallel. It says,
1st Panel up to 2 units requires a 60amp breaker  in the load panel, 3 units 90A, 4 - 5 units 150A
but in the wiring diagram it shows AC output from each unit going to the load. Would that not be 3 x 30A breakers for 3 units or the AC output goes to a bus bar and then that 6AWG wire would go to a 90A breaker in the panel? That seems unsafe to use bus bars for AC.
Same for AC input. Do I need 3 x 30A breakers in my utility panel to send AC to each unit or just 1 x 90A breaker going to a bus bar and then splitting into each unit?
diagram
breaker
I believe this is saying you can do up to 60A for 2 inverters, 90A for 3 inverter and so on. I attached a link where someone explains how they installed their system.
EG4 3kW inverters in parallel 120/240 volts, EG4-48v batteries & bifacial solar panels runs AC
(@philip14505)
Thank you. I have seen this video and it is a different use case. He appears to have his inverters output set for split phase to a 240VAC double pole breaker. The hot of one inverter is one hot leg and the hot of the other.
I am installing just one inverter to start so it will be be just single-phase to the load panel and 30A breaker. I don't plan on ever moving any of my 240VAC circuits to the off-grid load panel. When I am ready to add more 120VAC circuits, I will need to add 2 more inverters.
I suspect that I will need to add 2 more 30A breakers into the load panel with one breaker per inverter.
My other question was about utility power. I plan to implement in several phases for cost since I have to save money for each stage.
Stage 1: A single inverter with 1 x 48v 100ah battery to act as a battery backup for my freezers. No real savings here.
Stage 2: Add solar panels and reconfigure the inverter to make solar input primary power, battery as second, and utility as third.
Stage 3: Add 2 x 48v 100ah batteries in parallel so I can increase no solar capacity for overnight and move the rest of my garage 110VAC circuits over to the off-grid load panel. Total draw should still be within the 30amps.
Stage 4: Add 2 inverters so I can increase the load panel capacity to 90amps.
Stage 5: Move additional 60amps worth of 110VAC circuits from the house to the off-grid panel. Start adding more solar and batteries as needed.
SO .. according to the diagram, it seems AC INPUT to each inverters requires a dedicated 30A breaker from the utility panel and AC OUTPUT from each inverter has to go to a dedicated 30A breaker in the load panel.
I am just going to pre-run the 10AWG wiring for the future inverters in the conduit just in case. It just sucks to run too small a conduit and realize you need to more wires so you end up running more conduit.
(@k7thsolar)
@philip14505 I think you are logically correct in your approach to have three 30A breakers so that you can add the second and third inverter as well as giving you the ability to isolate an inverter for any reason.  I just purchased my first inverter this week and was planning on the same type of migration.  Good luck!