Question Configuring the (NO2,COM2) dry contacts in 6000xp

6 Posts
3 Users
0 Reactions
16 Views
Posts: 6
Topic starter
(@krzysiek_kta)
Active Member
Joined: 6 months ago

Hallo Eric,

Thanks for reply.

Actually I wanted to use dry port to trigger the external relay switch based on the SoC of the battery. Is there any way to program the NO2/NC2 dry port behavior ?

As per Manual it should be govern by "Gen charge start voltage/SoC" setting. Obviously it doesn't work. NO2 opens only when the inverter is powered off and stays closed regardless of "Gen charge start voltage/SoC" setting.

I believe same applies to NO1 - the Monitoring Site shows : "GEN Dry Contact: ON" when there is no Grid connected to the inverter regardless of the Gen charge start voltage/SoC setting in the system.

The "GEN Dry Contact: OFF" shows when the grid is connected to the system  - so in this case the contact works as as intended.

Tried "Gen charge start voltage/SoC" setting as voltage while in Lead Acid battery mode and SoC in Lithium1 battery mode - all same. Only powering down the inverter triggers NO2 dry contacts to open.

Just my observation.

 

Brgds

 

K

 

 

 