EG4 6000XP Rapidly Entering and Exiting bypass mode!

11 Posts
3 Users
0 Reactions
365 Views
Posts: 37
Topic starter
(@dannybeardsley)
Trusted Member
Joined: 2 months ago

A large current draw (4400w) in the morning caused a rapid cycling of bypass mode. It would switch back and forth every 2 seconds.
I have max discharge current from batteries set to about 2300w at the moment, so it makes sense that it would go into bypass mode. But it was leaving bypass mode after 1 second and then immediately re-entering bypass mode. It did this for 5 minutes before I noticed (lights flickering) and was able to reduce the load. At this time there was about 500w of solar available.

Notably, the screen (and the app) would briefly display 3500W coming from the solar panels. This was early morning and I know that isn't possible given the angle of the sun, so it's likely a measurement error. Any ideas of what to do here? I've had the 6000XP enter and exit bypass mode many times and it's usually been fine, it usually tries to exit bypass mode like 5 minutes after first entering. I added a new circuit to the loads yesterday (a 240V electric water heater) and it seemed to have problems when it started to use the 4000W heating element.

10 Replies
Eric
Posts: 202
 Eric
(@eric)
Estimable Member
Joined: 5 months ago

What Firmware is your inverter on?

Have you had this issue before, or did it just recently happen?

Did you get any alarms while this issue happened?

Reply
Posts: 37
Topic starter
(@dannybeardsley)
Trusted Member
Joined: 2 months ago

Firmware is at version: ccaa-180D0E. I tried to update 3 or 4 few times... but it always "Failed".

This is the first time that I can recall this happening. I've had it in use for a month or so but just yesterday moved an additional circuit (hybrid water heater) to be powered by the 6000XP.

Reply
Posts: 37
Topic starter
(@dannybeardsley)
Trusted Member
Joined: 2 months ago

> Did you get any alarms while this issue happened?

None during this period. I do get a fair number of EPS Overload events because I have a discharge limit of 45A (small batteries, small wires). When my loads exceed this it usually flips over toe bypass mode for ~5min as expected, but this was quite different.

I have remote support enabled if you'd like to take a look.

There's also a possibly related symptom. I just installed a lot more solar, so my batteries are fully charged fairly early (and move into the "float" voltage). It seems while I'm in this phase that it's a *lot* easier to hit EPS Overload, even when my loads don't seemingly exceed the limits. I just had an instance where a load spike resulted in it being in bypass mode for ~1 hour even though the spike was seemingly short (See screenshot).

image
Reply
Posts: 37
Topic starter
(@dannybeardsley)
Trusted Member
Joined: 2 months ago

I've updated to the latest firmware (ccaa-190D0E) last week and can confirm it's still occasionally happening. I just had it happen this morning, and the symptoms are the same, rapid cycling of bypass mode on and off. Still no alarms or events while this is happening.

A hot water kettle and the toaster (both resistive loads) at the same time (though on separate circuit legs) pushed me over the discharge limit. It would flip to bypass mode and then back every second or so until I dropped one of the loads. I'm able to reproduce this consistently (I just tried again).

It's clear to me why it would switch to bypass mode as I'm exceeding the configured discharge limit. But it's not clear to me why it would immediately switch back to batteries. This seems like a bug and I have to imagine it's bad for the relays to constantly switch back and forth, I know all my lights dip for at least a couple of the 60hz cycles. I'm hesitant to move any more of my circuits over while this is still happening.

 

Reply