@eg4eric it's 3.5 ton (what a weird unit) and consumes about 4kw. There have been no alarms and no events in the event log when I experience the pro...
To be clear, sustained loads (more than a few seconds) above 12kw cause the inverter to almost seamlessly flip to grid bypass mode. It's the startup o...
I have the same issue with the 6000XP and 12000XP. Would love a way to backup settings (download a CSV maybe?). I know it's a bigger ask, but versioni...
> The specs for the water heater I was considering say 240v, 27amps. My question is, can I damage the inverter if I attempt to use this? I wouldn't...
Unless of course that I'm wrong and this inverter isn't intended to provide continuous power and thus should only be used in "Emergencies" or as a "Ba...
This continues to happen every so often.It looks like occasionally the inverter is reading a RS485 packet full of `6659` repeating and doesn't validat...
Woah! The latest firmware (released today!) Seems possibly to have fixed the problem!Not a single EPS overload today!
I have this inverter. It does not “trip the breakers”, the 200A battery breaker is not electrically controlled. It does shut down the inverter (all ou...
I have more data. I experimented today with turning off the solar disconnect and it instantly solved the problem. The 6000xp had been ramping down the...
@eric Yes, now that I have a BMS, it does a better job of getting the voltage. I've also ramped my max amps up to 200A (charge and discharge). And yet...
If EG4 is working on this problem, I'd love some statement that says so and I'll wait for the next firmware. If more data is needed, I'm happy to give...